F041 Endress+Hauser — PT100/PT1000 probe faulty (open circuit or short circuit)

At a glance

Severity
FAULT STOP
Domain
INSTRUMENTATION
Reference standard
IEC 60751 / DIN EN 60751
Product / context
Sensor break (open circuit)

What it means

The RTD temperature probe (PT100 or PT1000) shows an abnormal resistance value: infinite resistance (open circuit) or near-zero resistance (short circuit). The transmitter or PLC analog input detects the fault condition and displays an out-of-range temperature (typically 9999°C or -200°C). The associated temperature control is compromised.

Probable causes

Reference values

PT100 IEC60751 ohm{"0C":100,"100C":138.5,"coefficiente":"0.385 Ω/°C"}
PT1000same values ×10
notaWith 3/4-wire sensors compensate the lead wire resistance.

Where to start

Disconnect the probe from the transmitter or PLC input and measure the resistance across the probe with a multimeter. For a PT100 at room temperature (~20°C), the expected value is approximately 107.8Ω. Is the resistance reasonable?